Necesito ayuda para calcular la matriz de admisión de bus para el siguiente sistema de área de 4 máquinas 2 de Kundur:
%% branch data
% From(Bus) to(bus) r(p.u) x(p.u) b(total charging line susceptance)
mpc.branch = [1 2 0.0025 0.025 0.00175*25;
2 5 0.0010 0.010 0.00175*10;
5 6 0.0220 0.220 0.00175*10;
3 4 0.0025 0.025 0.00175*25;
4 6 0.0010 0.010 0.00175*10];
%%Bus V phase P gen Q gen P load Q load
[p.u.] [rad] [p.u.] [p.u.] [p.u.] [p.u.]
Bus 01 1.03 0.86019 7.4911 0.71811 0 0
Bus 02 1.01 0.68099 2.9291 1.3674 0 0
Bus 03 1.03 -0.11868 6.2548 0.63815 0 0
Bus 04 1.01 -0.26796 5.258 1.0209 0 0
Bus 05 0.99698 0.57945 0 0 6.2855 -1.6
Bus 06 0.9973 -0.3808 0 0 14.806 -2.6
%% State-variables of the generators
Power angle(rad):
delta_Syn_1=1.7281, delta_Syn_2=1.089,
delta_Syn_3=0.66592, delta_Syn_4=0.41743
Angular frequency (p.u): 1 represents the steady-state
omega_Syn_1=1, omega_Syn_2=1, omega_Syn_3=1, omega_Syn_4=1
Transient voltage: q axis—e1q, and d axis—e1d.
e1q_Syn_1=0.86696, e1d_Syn_1=0.64857,
e1q_Syn_2=1.0075, e1d_Syn_2=0.33055,
e1q_Syn_3=0.88761, e1d_Syn_3=0.6004,
e1q_Syn_4=0.91878, e1d_Syn_4=0.52742
La matriz que calculé:
Yt =[3.9604-39.5821i -3.9604 +39.6040i 0 0;
-3.9604+39.6040i 10.2978-42.5695i 0 0.4488 + 4.1550i;
0 0 3.9604-39.5821i -3.9604+39.6040i;
0 0.4488+4.1550i -3.9604 +39.6040i 18.1924 -43.2853i]
Las corrientes generadoras It calculadas a partir de It = Yt * Ut no satisfacen la generación de energía. ¿Alguien puede indicar si el cálculo de Yt es incorrecto o el análisis de flujo de potencia es incorrecto?